The yearly load duration curve of a certain power station can be approximated as a straight line;
Fantastic news! We've Found the answer you've been seeking!
Question:
The yearly load duration curve of a certain power station can be approximated as a straight line; the maximum and minimum loads being 100 MW and 60 MW respectively. To meet this load, three turbine-generator units, two rated at 40 MW each and one at 30 MW are installed. Determine the plant factor of the station