Question: 1 5 . 4 0 It has been determined by test that the synchronous reactance ( X _ { s } ) and

15.40 It has been determined by test that the synchronous reactance \( X_{s}\) and armature resistance \( R_{a}\) of a 2,300-V,500-VA, three-phase synchronous generator are 8.0 and \(0.1\Omega \), respectively. If the machine is operating at rated load and voltage at a power factor of 0.867 lagging, find the generated voltage per phase and the torque angle.