Question: 10. Where a single-phase, 240-volt air-conditioning unit has a full-load current rating of 35 amperes, what is the MINIMUM size 75C rated copper conductors

10. Where a single-phase, 240-volt air-conditioning unit has a full-load current rating of 35 amperes, what is the MINIMUM size 75C rated copper conductors required to supply the air- conditioning unit? 10 AWG 8 AWG 6 AWG 4 AWG A. B. C. D.
Step by Step Solution
3.41 Rating (164 Votes )
There are 3 Steps involved in it
the answer is 8 AWG Justification Inputs singlephase 240volt air conditioning unit fu... View full answer