Question: 10. Where a single-phase, 240-volt air-conditioning unit has a full-load current rating of 35 amperes, what is the MINIMUM size 75C rated copper conductors

10. Where a single-phase, 240-volt air-conditioning unit has a full-load current rating

10. Where a single-phase, 240-volt air-conditioning unit has a full-load current rating of 35 amperes, what is the MINIMUM size 75C rated copper conductors required to supply the air- conditioning unit? 10 AWG 8 AWG 6 AWG 4 AWG A. B. C. D.

Step by Step Solution

3.41 Rating (164 Votes )

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock

the answer is 8 AWG Justification Inputs singlephase 240volt air conditioning unit fu... View full answer