Question: 2 . ( a ) A 1 2 kVAt 1 , 0 0 0 / 1 0 0 V , 5 0 Hz , single

2.(a) A 12 kVAt 1,000/100 V,50 Hz, single-phase transformer has the following test results:
OC test (on LV side): 100 V,0.7 A,85 W
SC test (on HV side with 100 V side short circuited): 60 V,12 A,95 W
Determine the following:
Core loss of the transformer.
(1 mark)
(ii) Equivalent resistance and leakage reactance referred to as High Voltage (HV) side.
(5 marks)
(iii) Equivalent resistance and leakage reactance referred to as Low Voltage (LV) side.
(2 marks)
(iv) Voltage Regulation of the transformer at full load at 0.8 power factor lagging.
(3 marks)
(v) Transformer terminal voltage at full load at 0.8 power factor lagging.
(1 mark)
(vi) Efficiency of the transformer at full load 0.8 power factor lagging.
(5 marks)
[Cont...
[Cont...2.
(b) A 500 kVA single-phase transformer has an efficiency of 95% at full-load with unity power factor and also at 60% of full-load with unity power factor. Determine the efficiency of the transformer at 75% of full-load at 0.8 power factor.