Question: 3 0 pts Water Supply System Upfeed system When the pressure from the city mains is sufficient to overcome all friction in the system with

30 pts
Water Supply System
Upfeed system
When the pressure from the city mains is sufficient to overcome all friction in the system with the calculated flow and still maintain the minimum pressure needed at the highest outlet, the system used is called an upfeed system.
Will 40 psi minimum maintained city mains pressure be sufficient for the structure shown?
Assumptions
5 psi friction loss on the water meter
9100ft pressure loss in piping
Fittings add 50% to effective pipe length
Distance from water main to the farthest fixtures:
Second-floor shower head =90ft
Garden hose bibb =60ft
9 ft floor height
5 ft from mains to first-floor
From Table 9.1:
Required minimum flow pressures are:
8 psi-showerhead
15 psi -5/8-in sillcock
Highest fixture is the shower head:
Shower head -7 ft above the second floor
Total height =5ft+9ft+7ft=21ft
Garden hose bibb is 8 ft above the water main
Schematic plumbing section of an upfeed water distribution system using city mains pressure. The building is a two-story residence.
[ THATS THE PICTURE]
Shower (13pts)
Fixture pressure = Mains pressure - Static head - Total friction
House Bibb (13 pts)
Fixture pressure = Mains pressure - Static head - Total friction
Would the mains pressure be adequated if the hose bibb was a 3/4-in, requiring 30 psi? (6 pts)
3 0 pts Water Supply System Upfeed system When

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Civil Engineering Questions!