Question: 3 . 2 3 Figure 3 . 3 2 shows the oneline diagram of a three - phase power system. By selecting a common base

3.23 Figure 3.32 shows the oneline diagram of a three-phase power system. By selecting a common base of 100 MVA and 22 kV on the generator side, draw an impedance diagram showing all impedances including the load impedance in per-unit. The data are given as follows:
\table[[G:,90 MVA,22 kV,x=0.18 per unit],[T1:,50 MVA,22220kV,x=0.10 per unit],[T2:,40 MVA,22011kV,x=0.06 per unit],[T3:,40 MVA,22110kV,x=0.064 per unit],[T4:,40 MVA,11011kV,x=0.08 per unit],[M:,66.5 MVA,10.45 kV,x=0.185 per unit]]
Lines 1 and 2 have series reactances of 48.4 and 65.43, respectively. At bus 4, the three-phase load absorbs 57 MVA at 10.45 kV and 0.6 power factor lagging.
FIGURE 3.32
Problem 3.23
3 . 2 3 Figure 3 . 3 2 shows the oneline diagram