Question: ( 4 0 pt ) A facility is to be maintained at 2 5 C dry bulb temperature ( d b ) and 5 0

(40pt) A facility is to be maintained at 25C dry bulb temperature (db) and 50% relative humidity. The space is occupied by 30 persons who each produce 65 W of sensible heat and 0.05kgh of moisture (heat of vaporization, hfg=2417.91kJkg). The design requires the use of 100% fresh air. The outdoor air has a temperature and relative humidity of 31C and 70%, respectively. Determine (a) the quantity and the state of the air supplied to the space, (b) the required capacity of the cooling and dehumidifying equipment, and (c) the coil sensible heat ratio. Include the psychrometric chart with your solution.