Question: 4 6 A ( 1 1 0 - mathrm { kVA } , 1 ) - phase transformer has a ratio of

46 A \(110-\mathrm{kVA},1\)-phase transformer has a ratio of \(11000/440\mathrm{~V}\). The iron loss measured on open-circuit is 1100 W . With the secondary winding short-circuited, a voltage of 500 V at normal frequency applied to the primary produces full-load current, the wattmeter reading 1000 W . Calculate (a) the secondary terminal voltage, (b) the efficiency, when a current of 250 A at a lagging power factor of 0.8 is taken by a load connected to the low-voltage terminals, the primary voltage being 11000 V .
[(a)425 V ; (b)\(97\cdot 6\%\).]