Question: A 2 5 0 ' deep test borehole was originally drilled in 1 9 9 6 . In 2 0 1 3 , we performed

A 250' deep test borehole was originally drilled in 1996. In 2013, we performed a TRT. Here's
the information we have:
Prior to running the TRT, the temperatures at depths were measured on 10' to
20'intervals. This data is found in the file: Undisturbed_temperatures . xlsx
The measurements have been reduced to 1 minute intervals (from 10-second intervals).
Two pairs of carefully calibrated thermocouples were used, from which two values of
mean fluid temperature were produced. You'll see there are slight differences, which
reflect the limitations we have in calibrating temperature sensors. The measured total
power in Watts is based on the electricity used by the fixed capacity heating element,
the variable-capacity heating element, and the pump. The data are summarized in
TRT_data_reduced.xlsx.
The borehole was drilled with a 4.5'' bit and grouted with enhanced thermal grout with
thermal conductivity of 0.85Btuh*ftF. The grout was "63.5%TG85, the "world's
first thermally enhanced grout" from GeoPro. However, the formation contains layers
of sandstone, shale, and clay, and the borehole diameter may be nonuniform. They
expected to have to add 20 bags of grout to fill the hole. On the day that it was done,
they used 21 without filling the hole, and it settled to be 55'(17 m ) below the ground
surface. They later filled this in with another 5 bags, by pouring dry grout into a wet
borehole. Probably not an ideal procedure! [But, as I think I mentioned in class...there
may be no such thing as a perfect test.]
The U-tube is 1'' SDR-11 HDPE. The shank spacing was not controlled, as far as I know.
Determine the average undisturbed ground temperature for the borehole. Please consider
how the individual measurements should be weighted.
Estimate the effective thermal conductivity based on the period from 12 hours to the end of
the measurement period.
Estimate the effective borehole thermal resistance based on the period from 12 hours to
the end of the measurement period.
Estimate the effective thermal conductivity sequentially, starting with the period 12 hours
to the end of the measurement period, then 12 hours +1 minute, 12 hours +2 minutes, etc.
(If you want to use a larger time interval, say 12 hours +10 minutes, 12 hours +20 minutes,
etc., that's fine.)
A 2 5 0 ' deep test borehole was originally

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Mechanical Engineering Questions!