Question: A bar type current transformer of toroidal construction requires 400A to magnetize it, and 300 A to supply the iron loss for each volt per

A bar type current transformer of toroidal construction requires 400A to magnetize it, and 300 A to supply the iron loss for each volt per turn induced in the secondary winding and rated frequency. Across the secondary terminal is connected an impedance of 2 ohm with a phase angle . and the resistance of secondary winding is 0.5 ohm. The nominal ratio is 1000/5 A, and it is required to minimize both ratio and phase errors. Determine the necessary values of secondary winding turns and phase angle.

Step by Step Solution

3.45 Rating (148 Votes )

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock

Formula Ratio Error RE N1N2 x IsIp x 100 Phase Error PE s p x 100 Where RE Ratio Error N1 Number of turns of Primary winding N2 Number of turns of Sec... View full answer