Question: A plate - load test was conducted in a sandy soil in which the size of the bearing plate was 0 . 3 m 0

A plate-load test was conducted in a sandy soil in which the size of the
bearing plate was 0.3m0.3m. The ultimate bearing stress for the test was
found to be 184.5kPa. Estimate the total allowable load (Qall) for a footing
of size 1.8m1.8m. Use a factor of safety of 4.
For clayey soil: ,qu(F)=qu(P)
For sandy soils: ,qu(F)=qu(P)BFBP
B?bar(F)= width of the foundation
Bp= width of the test plate
149.0kN
598.0kN
897.0kN
185.0kN