Question: A shopping complex is planned to be built in Kuala Kangsar, Perak and their loads are listed in Table 2. There is a 1000 kVA
A shopping complex is planned to be built in Kuala Kangsar, Perak and their loads are listed in Table 2. There is a 1000 kVA distribution transformer at the substation that is located nearby the shopping complex. Currently, the maximum demand for the distribution transformer is 500 kVA and the capacity of the transformer loading cannot be beyond 90% of its rating. Overall, the diversity factor for the whole load is estimated to be 1.5. The building contractor submits their proposal to tap the electricity supply from the existing distribution transformer. As an engineer at the utility company, analyze the coincident maximum demand of the whole complex in order to decide whether their proposal can be approved and give some justifications to support your decision. Table 2
| Load | No. of Load ] | Diversity Factor | Demand Factor ] |
| Elevator motors rated 30 hp with 90% efficiency | 5 | 1.81 | - |
| 5 kW Fast food shop | 1 | - | 0.9 |
| 3 kW Food Court stall | 10 | - | 0.5 |
| 2 kW Boutique shop | 60 | - | 5.2 |
100 W lighting for parking lots no . of load =50 |
Step by Step Solution
There are 3 Steps involved in it
Diversity factor 15 Demand factor for the distribution transformer is 500kVA1000kVA 05 Capaci... View full answer