Question: A single phase, 2 5 kVA, 2 2 0 4 4 0 V , 6 0 Hz transformer gave the following test results. Open circuit

A single phase,25kVA,220440V,60Hz transformer gave the following test results.
Open circuit test (440V side open): 220V,9.5A,650W
Short-circuit test (220V side shorted): 37.5V,55A,950W
(a)Derive the approximate equivalent circuit in per-unit values.
(b)Determine the voltage regulation at full load, 0.8PF lagging.