An 18,000 Btu/h split air conditioner running at full load is used to keep a room at
Fantastic news! We've Found the answer you've been seeking!
Question:
An 18,000 Btu/h split air conditioner running at full load is used to keep a room at 22°C in an environment at 33°C. The power input to the compressor is 3.4 kW.
Determine
(a) the rate of heat rejected in the condenser, in kJ/h,
(b) the COP of the air conditioner, and
(c) the rate of cooling, in Btu/h, if the air conditioner operates as a Carnot refrigerator for the same power input.