Question: ( b ) Static pile load test was carried out on a 4 0 0 m m - by - 4 0 0 m m

(b) Static pile load test was carried out on a 400mm- by -400mm solid concrete pile (with con=4ksi ) installed 20m into a loose-to-medium sandy soil. The pile was driven into the soil. Selected load displacement data are shown in the table below. (a) determine the allowable load if the serviceability limit is 12mm.(b) Is the maximum load the ultimate load? Justify your answer. (c) estimate the structural capacity of the tested pile.
\table[[Load (ton),0,24,50,75,100,125,150,175,191,195,175],[Displacement (mm),0,0.3,0.85,1.21,1.85,2.72,3.93,5.67,13.54,24.7,24.1]]