Question: An isolated synchronous generator with transient reactance equal to 0.2 pu on a 100 MVA base is connected to the high voltage bus through
An isolated synchronous generator with transient reactance equal to 0.2 pu on a 100 MVA base is connected to the high voltage bus through a step-up transformer of reactance 0.05 pu on a 100 MVA base. The fault level at the HV bus is, MVA (Calculate to 2 decimal places)