Question: Consider the simple feeder shown in Figure 1.1 with conductor data as in Table and consumption data as in the following tables. A second feeder

 Consider the simple feeder shown in Figure 1.1 with conductor data

Consider the simple feeder shown in Figure 1.1 with conductor data as in Table and consumption data as in the following tables. A second feeder section (CE) is connected to point C, with 35mm2 conductor cross section. The minimum and maximum consumptions at point E are 900 and 500kW, respectively. Calculate the first and the second hosting capacity for the different feeder sections. A B D Feeder section AB BC CD Conductor size Ampacity Maximum permissible power 185 mm 388 A 10 MVA 95 mm2 268 A 7 MVA 35 mm 151 A 3.9 MVA B D Maximum active power Maximum reactive power Minimum active power Minimum reactive power 2 MW 1.3 Mvar 500 kW 300 kvar 3.5 MW 2 Mvar 900 kW 2.5 MW 1.3 Mvar 700 kW 500 kvar 500 kvar Pgen, max Pcons, min + P2 + Qzons, max dons, min Pgen, max