Question: For a 1 3 . 8 k V , 0 . 8 5 power factor, 3 - phase, Y - connected generator with a rating

For a 13.8kV,0.85 power factor, 3-phase, Y-connected generator with a rating of 120 MW a differential protection (86) is employed. During through fault conditions, CT2 saturates, yielding an induced EMF equal to 75% of CT1. The stability factor is 2.5. The relay is set at 10% of 5 A , with a burden of 3 VA.
xd=20%
xd'=30%
x2=20%
x0=10%
CT ratio =75005A
RCT=1.5
Lead resistance CT1 to relay: 1.5
Lead resistance CT2 to relay: 2.5
For a 1 3 . 8 k V , 0 . 8 5 power factor, 3 -