Question: For the short, concentrically loaded square tied column shown, the applied dead load is 1 5 0 kips ( D L = 1 5 0

For the short, concentrically loaded square tied column shown, the applied dead load is 150 kips (DL=150kips ), and the applied axial live load is 250kips (LL=250Kips ). Assuming that the longitudinal reinforcing bars are all the same size. Determine the minimum size of each longitudinal reinforcing bar. fc'=4000,fy=60,000(20pts)
f'C=4000 PSi =4Asi
fy=60000 PSi =60ksi
Gross Area =1818=324in2=Ag
Square Tied Column:
(A) No.3
=0.65
(B) No.4
DL=150k,LL=250k
(C) No 5
(D) No 6
pu=1.2(150)+1.6(250)
pu=580k=pn
[0.85f'C(Ag-Ast)+fy(As2)]
.50.8[0.854(324-Ast)+60Ast]
.5in2
Pn=0.8[0.85f'C(Ag-Ast)+fy(As2)]
580=0.650.8[0.854(324-Ast)+60 Ast ]
Ast =0.25in2
Provide 8#3 bars =0.88in2
For the short, concentrically loaded square tied