Question: Looking at the unit generator above. We have an external fault on the grid. Assuming: CT by the generator is 6 0 0 0 /

Looking at the unit generator above. We have an external fault on the grid.
Assuming:
CT by the generator is 6000/5,
CT next to the grid connection is 600/5,
CT next to the Unit Aux. Xfmr is 6000/5.
The 87 TG is set to 25% slope with a pick up of 0.5A.
No fault current is flowing to the auxiliary bus to simplify calculations.
We measure the fault current coming out of the generator to be 47.4kA.
How much current is flowing through the operating coil of the 87TG relay?Looking at the unit generator above. We have an external fault on the grid.
Assuming:
CT by the generator is 6000/5,
CT next to the grid connection is 600/5,
CT next to the Unit Aux. Xfmr is 6000/5.
The 87 TG is set to 25% slope with a pick up of 0.5A.
No fault current is flowing to the auxiliary bus to simplify calculations.
We measure the fault current coming out of the generator to be 47.4kA.
How much current is flowing through the operating coil of the 87TG relay?