Question: P 1 1 . 6 - 7 A motor connected to a 2 2 0 - V supply line from the power company has a

P 11.6-7 A motor connected to a 220-V supply line from the power company has a current of 7.6 A. Both the current and the voltage are rms values. The average power delivered to the motor is 1317 W.(a) Find the apparent power, the reactive power, and the power factor when o 377 rad/s.(b) Find the capacitance of a parallel capacitor that will result in a unity power factor of the combination. (c) Find the current in the utility lines after the capacitor is installed. Answers: (a) pf 0.788(b) C 56.5 mF (c) I 6.0 A rms