Activity 12-2-Elevation Changes It is desired to measure a corrosive fluid in a process pipeline. Because of the corrosive fluid, the pressure trans- mitter needs to be protected with a chemical seal with a capillary connecting it to the transmitter. The pressure to be measured is 0 psig to 30 psig and the process connection is 15' above the transmitter location. The capillary fluid has a specific gravity of 1.75. The transmitter was calibrated when the chemical seal was at the same ele- vation as the transmitter. 0 psig to 30 psig -20 psig 15 1. What error in pressure measurement in psi would be sensed by the transmitter? 2. What simple changes can be made to allow the transmitter to read correctly