Question: Please provide calculations for given solutions. Consider a a HSS 1 4 0 . 5 0 0 A 5 0 0 Gr B ( F

Please provide calculations for given solutions.
Consider a a HSS140.500 A500 Gr B (Fy=46ksi) section filled with normal weight concrete fc'=4ksi and wc=145pcf. Column length =30ft. Both column ends are fixed.
(i) Determine design strength of the composite column. Answer: Pn=881 kip. Intermediate answers: Pe=3122kip,Pno=1421 kip.
(ii) A load of 500 kip is applied to the steel section directly from beam that is 12 inch deep.
Using 4 in. long 34 in. diameter Fu=65ksi shear studs determine appropriate number of the anchors for shear transfer. Answer: Provide 3 sets of 4 connectors for a total of 12 connectors. Intermediate answers: Rn,DirectBond=99.36kip.Vr'=179.4 kip, for one shear stud
Qn=18.67 kip.
Please provide calculations for given solutions.