Question: PROBLEM 3 . ( 2 0 POINTS ) A factory has two zones. Zone 1 and 2 are both maintained at 7 5 F d

PROBLEM 3.(20 POINTS)
A factory has two zones. Zone 1 and 2 are both maintained at 75FdB. The design supply
air flow rates to Zone 1 and 2 are 3200 and 2000 CFM, respectively. At a certain hour in
summer, the cooling loads for Zone 1 and 2 are 60,000Btuhr and 30,000Btuhr,
respectively.
Assume dry air conditions and air density of 0.075lbmft3
(a) If a single-duct constant-volume system with local reheat boxes is used with
discriminator control, what would the required amount of reheat (Btuhr) to be provided in
each zone at the hour?
The design cold air supply temperatures are 55FdB.
(b) If a VAV system with 20% minimum position is used with discriminator control, what
would the required amount of reheat (Btuhr) be provided by a reheater in each zone at the
hour? The design supply air temperature is 55FDB.