Question: PROBLEM 5 . ( 2 0 POINTS ) a . 1 5 points An office has one external wall 5 m long, containing a window

PROBLEM 5.(20 POINTS)
a.15 points
An office has one external wall 5 m long, containing a window of area 4m2; the width of tho office from the window to the wall adjacent to the corridor is 4 m , and the ceiling height is 3 m There are similar offices above, below and on either side. The temperature in the corridor i16C, the temperature in the room is 20C, and the external design temperature is -1C. If the heat transfer coefficients for the external wall, window and internal wall are 1Wm2K5.6 W/m ?2K, and 2.7Wm2K, respectively, and an air change rate of one per hour is require for ventilation, calculate the heat input to the room.