Question: Problem 9 - 2 1 Do only LRFD . Address only Moment capacity. ( i . e . you do not have to check shear

Problem 9-21 Do only LRFD. Address only Moment capacity. (i.e. you
do not have to check shear or deflections).
9-21. The cantilever beam shown in Fig. P9-21 is a W21555 of A992-Grade 50
steel. Lateral bracing is supplied at the fixed end only. The uniform load is a
service dead load and includes the beam self-weight. The concentrated loads are
service live loads. Determine whether the beam is adequate using LRFD. Assume Cb=1.0.(Ans. LRFD OK,409.6ft-k>395.0ft-k)