Question: Q 4 . ( a ) The owner intends to change the use of his building and the new building information is shown in the

Q4.(a) The owner intends to change the use of his building and the new building information is shown in the following:
Building Type: Shopping mall
Gross floor area: 2,400m2
Room height: 5 m
Compartment: One per floor
Openable window area: 130m2 per floor
Design fire load =1200MJm2
(i) Justify with reasons whether a smoke extraction system is needed for the shopping mall. (6 marks)
(ii) The shopping mall is designed with a size of 8m4m confined fire area having a convective heat output of 800kWm2. The ambient air temperature is 17C. Using the following Morgan formula, determine the temperature rise of smoke layer, density of smoke and volumetric flow rate of smoke production if the bottom smoke layer to floor distance is kept at 3 m .
(5 marks)
Given:
M=0.188Py32,=QMC,V=MTo+oTo
s=oToTo+
where
M= mass flow rate of smoke production (kgs)
P,= perimeter of fire (m)
y,= distance between the floor and the bottom of smoke layer (m)
Q,= convective heat output of fire (kW)
,= temperature rise of the smoke layer above ambient temperature (K)
Cp,= specific heat of smoke (kJkgK)=1.0kJkgK
V,= volume flow rate of smoke (m3s)
To,=absolute temperature of ambient air (K)
o density of ambient air (kgm3)=1.22kgm3at290K
s density of smoke (kgm3)
0C,=273K
To be continued...
PTHDOA-Piped Services and Fire Safety Installations B (MBS4243)
Page 8 of 14
January 2021
Q 4 . ( a ) The owner intends to change the use

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Civil Engineering Questions!