Question: Q: In a balanced three - phase Y - Y connection consuming 6 0 0 kW , the effective value of the line -

Q: "In a balanced three-phase Y-Y connection consuming 600 kW , the effective value of the line-to-line voltage at the load terminals is 400 V . If the power factor of the load is 0.8 lagging, answer the following questions. Assume that the equivalent line impedance is 0.02+j0.05
(Equivalent power consumption =6003=200kW, phase voltage =400?23=230.94V)
Calculate the equivalent load impedance.
Answer: 0.17+j0.128[]
Determine the phase current of the load.
Answer: 866-j649.5[A], current magnitude =1082.5A
Find the magnitude of the line-to-line voltage at the source.
Answer: 489 V