Question: Question 1 1 0 pts The CTR = 3 0 0 : 5 and the V T R = 2 3 0 K V :

Question 1
10 pts
The CTR =300:5 and the VTR=230KV:120V and our zone of protection is Bus A , the transmission line, and Bus B.
We measured a fault on the transmission line. The relay recorded Isec=37.0A and Vsec=44.8 V (we always measure line to line voltage).
The line has an impedance of ZLine=0.5 per mile.
From Bus A (where the relay is) how far down the line is the fault? Answer in miles.
Hint: Calculate the Zprimary impedance first then figure out the distance of the fault from Bus A