Question: Question 2 ( 1 2 . 5 points ) Question 2 : Using Limit States Design criteria and OBC 2 0 1 2 , Part

Question 2(12.5 points)
Question 2:
Using Limit States Design criteria and OBC 2012, Part 4, for the floor and roof layouts below calculate
the total factored load at the base of column 1(Col 1) due to the following service loads:
Roof:
Dead load DL=3.28KPa (concrete, roofing, insulation)
Live load due to occupancy LL=1KPa
Total Snow load S =2.44KPa
Second floor:
Dead load DL =2KPa (deck, finishes)
Live load due to occupancy LL=3.6KPa
Assume the following weights for the structural elements:
Joist =0.17KNm
Main Beam =0.24KNm
Column =0.48KNm; Height of column =5.8mfloor
Column =0.48KNm; Height of column =5.8m? floor
Load combination for a roof: 1.25DL+1.5S+1LL
Load combination for a floor: 1.25DL+1.5LL
All joists, beams and top of column are flusit at the top. B
CO 1
ROOF
ROOF
3m
5m5m