Question: Question 2 Shown in Figure Q 2 is a main LV switchboard fed from a 2 0 0 0 kVA 1 1 k V 4
Question
Shown in Figure Q is a main LV switchboard fed from a kVA distribution transformer and protected by a A MICB main incoming circuit breaker One mlong feeder circuit is wired with two PVCSWAPVC cables on tray, and is protected by a A ACB air circuit breaker The earth fault loop impedance at the main LV switchboard is mohm. Both A and A circuit breakers are controlled with IDMT relays for earth fault protection. Electronic relays with SI and EI curves are available for selection.
a Determine the breaking capacity of A ACB.
marks
b Find out the min. fault current in the feeder circuit for the chiller plant.
marks
c Select the type, PS and TM of the earthfault relay for MICB so that the relevant requirement in CoP can be achieved. Explain the meaning of P using the CTs for MICB.
marks
d Select the type, PS and TM of the earthfault relay for ACB if the discrimination between MICB and ACB is achieved for the possible range of earth fault current in this feeder circuit. The grading time is assumed to be sec
marks
The timecurrent characteristic of relays is described by
The plug setting PS is in the range of with a step size of and the time multiplier TM is in the range of with a step size of Additional information is given in Appendix.