Question: Question 3 3 - phase Transformer Differential protection All que a ) Calculate the full - load ( or normal - load ) power transformer

Question 3
3-phase Transformer Differential protection
All que
a) Calculate the full-load (or normal-load) power transformer line currents.
b) Select CT connections and ratios so that the primary CT rating is greater than the 3-ph transformer full-load (or normal-load) line current.
c) Calculate the CT secondary currents at full load.
d) Keeping in mind the rule for CT connections, calculate the current flowing from the CTs to the relays.
e) Select relay taps so the ratio of tap settings is as nearly as possible equal to the ratio of currents that flow to the relay. Also, the relay taps should be as nearly as possible equal to the respective currents that flow under full-load (or normal load) conditions.
6
Select 4.6A tap for HV side
Since there is only one tap available on the LV side (8.7A) a quicker way to find the corresponding tap on the HV side is shown below:
Select 4.6A tap for HV side
Since there is only one tap available on the LV side (8.7A) a quicker way to find the corresponding tap on the HV side is shown below:
f) Calculate the resulting % unbalance
g) Determine the minimum relay pickup that will avoid nuisance tripping on no-load of 10% FL. Settings in increments of 0.1 A , with a minimum of 0.3 A , are available.
Question 3 3 - phase Transformer Differential

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Electrical Engineering Questions!