Question: Show the calculations to determine the minimum size Type THHN conductors and the rating of the overcurrent protective device (fuses) for the circuit supplying
Show the calculations to determine the minimum size Type THHN conductors and the rating of the overcurrent protective device (fuses) for the circuit supplying the boiler. Use two conductors per phase in two raceways. Also determine the size of the equip- ment grounding conductors to be installed in each raceway. The expected maximum temperature in the room where the boiler is located is 100F (37.8C). The boiler elec- trical panel and the distribution panel are rated 75C. All conductors are copper. Show the calculations to determine the minimum size Type THHN conductors and the rating of the overcurrent protective device (fuses) for the circuit supplying the boiler. Use two conductors per phase in two raceways. Also determine the size of the equip- ment grounding conductors to be installed in each raceway. The expected maximum temperature in the room where the boiler is located is 100F (37.8C). The boiler elec- trical panel and the distribution panel are rated 75C. All conductors are copper.
Step by Step Solution
3.46 Rating (143 Votes )
There are 3 Steps involved in it
To solve the problem in the image we can use the following steps Calculate the load current The load current is the current that will flow through the ... View full answer