Question: Step - 1 : At time zero, only blower is turned on . There is no cooling in this stage. Measure the temperature and air

Step-1: At time zero, only blower is turned on. There is no cooling in this stage. Measure the
temperature and air flow rate at various points as shown in Figure-1.
Step-2: Put the system in cooling mode to turn on the compressor. Run the system for several
minutes. Measure the temperature and air flow rate at various points as shown in Figure-1.
Step-3: Measure the amount of air passing across the evaporator coil. The airflow is measured in
cubic feet per minute (CFM).350 to 400 CFM per ton of cooling is required for proper air
conditioning system operation. For example, if you are checking a 3-ton system, the airflow
required is between 1050 and 1200 CFM.
Examine, in detail, the various components and operation of an HVAC system.
Identify the components and their function.
Trace flow paths through the various parts of the system.
Discuss the temperature measurements of the refrigerant at several locations within the
refrigeration system, and the temperature and humidity of the air stream.