Question: Suppose that a process plant has a large gas fired heater A hazard study has identified that the combustion chamber could explode if there is

Suppose
that a process plant has a large gas fired heater A hazard study has identified that the
combustion chamber could explode if there is a build up of unburnt gas and air after a loss of
flame event, leading to 5 fatalities The rate of this explosion happening has been analysed to be
about 001 per year (every 100 years) The plant has an estimated lifetime of 20 years This could
arise if the gas supply is not shut off as soon as the flame is lost The are 3 functional safety
system options being considered
Baseline Hazard
Baseline hazard consequence
Frequency =0.01 per yr (every 100 yrs
Baseline hazard
Severity =5 deaths
ALARP Option 1:
Reduces Frequency by factor of 10(to 0.001): Costs 100K
ALARP Option 2:
Reduces Severity by factor of 5(to 1 death): Costs 10K
Perform CBA for:
Option 1,
Option 2, Option 1 and 2
For purpose of CBA use
Cost of single death =1,000,000