Question: System: Fixed meter Target Superheat: 17F 2F Evaporator Saturation Temperature: 42F Vapor Line Temperature: 53F Target Subcooling: 15F 3F Condenser Saturation Temperature: 120F Liquid Line
System: Fixed meter
Target Superheat: 17F 2F
Evaporator Saturation Temperature: 42F
Vapor Line Temperature: 53F
Target Subcooling: 15F 3F
Condenser Saturation Temperature: 120F
Liquid Line Temperature: 106F
Is the system UNDER, OVER or CORRECT charge?