Question: table [ [ , 1 . Draw the network with all the data as provided. ] , [ , 2 . Run a load

\table[[,1. Draw the network with all the data as provided.],[,2. Run a load flow to determine your steady state conditions.],[Steps:,\table[[3. Perform short circuit analysis at different buses.],[4. Select and size all CT.]]],[,\table[[5. Connect relays where appropriate.],[6. Carry out coordinating studies to adjust relay settings.],[7. Check for relay operation for selected fault locations.]]],[Report:,Prepare a detailed report of your work.],[Team Work:,You may work in a group of two but no more.],[\table[[Report],[Submission:]],Tuesday, December 31,2024, class time sharp.]]
1
Apply inverse definite minimum-time (IDMT) relay with normal inverse characteristic given as
t=0.14(IIS)0.02-1TP
Where t= tripping time of relay, Tp= time
Network parameters: G: 2MVA, 10%;
T1:,2MVA,113.3KV,7%;,T2:,500KVA,
3.3/0.415KV,6%; Lines 1,2,3: 0.02ph;
Line 5: 0.2ph; Line 8: 0.2ph; System MVA
base =20MVA; Positive and negative sequence impedances are assumed equal.
In this network, for a fault at the point F1, relays R1,R2 and R3 must not operate in less than 0.5 s .
Reactance of G=1p.u; Reactance of T1=0.7 p.uReactance of Line 8=0.367 p.u; Reactance of Line 5=0.367 p.u; Reactance of T2=2.4p.u; Reactance of Line 1=2.323 p.u;
For example, the feeder relay and breaker, which are downstream, should clear a feeder fault before the supply-side relay and breaker (upstream) could trip. Generally, CTI of about 0.4 seconds
solve this question on paper, correct solution to give like
\ table [ [ , 1 . Draw the network with all the

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Electrical Engineering Questions!