Question: TC 8 . 2 . Use refrigerant R - 1 3 4 a to be the working fluid in a vapor - compression refrigeration cycle.

TC8.2. Use refrigerant R-134a to be the working fluid in a vapor-compression refrigeration cycle. Saturated vapor enters the compressor at 2 bar, and saturated liquid exits the condenser at 8 bar. The compressor has an isentropic efficiency of 80%. The mass flow rate of the refrigerant is 7kgmin.
condenser
(a) Determine the compressor power, in kW .
(b) Determine the exergy destruction in the compressor, in kW .
(c) Determine the refrigeration capacity, in tons.
(d) Determine the exergy destruction at the valve, in kW .
(e) Determine the coefficient of performance.
Note: 1 ton of refrigeration =200BTUmin or 211kJmin.
[Answers: (a)40.4kW,(e)4 tons, (d)0.4kW,(e)40.7kW,(c)4 tons tons, (d)0.4kW,(e)44kW,(b)0.7kW,(c)4 tons tons, (d)0.4kW,(e)4