Question: Term project 2 4 1 As a mechanical engineer, you have been asked to design a cooling tower to remove heat from the condenser of

Term project 241
As a mechanical engineer, you have been asked to design a cooling tower to remove heat from the condenser of a steam power plant under the following conditions:
(a) Fossil-fueled vapor power plant.
For the condenser:
The cooling water enters the condenser at 33C
The mass flow rate of the cooling water is 60kgs
The heat needs to be removed form the condenser at rate of 1.76 MW
For the cooling tower:
Air enters the cooling tower at a temperature of 22C and O?=55%
Air leaves the cooling tower at a temperature of 30C and O?=95%
Task#1: Determine the mass flow rate of air entering the cooling tower, in kgs.
Task#2: Determine the required makeup water, in kgs.
Task# 3: Vary the relative humidity for the air entering the cooling tower from 30% to 90% and plot the mass flow rate of air vs the relative humidity for the air entering the cooling tower.Assume water condenser 20degree and also write the code for the program