Question: The maximum fault current in a given circuit is 12 000 A. The nominal CT ratio is 1200/5 and the CT is to be
The maximum fault current in a given circuit is 12 000 A. The nominal CT ratio is 1200/5 and the CT is to be used with a tap of 800/5. The CT class is C-200, the resistance of the secondary is 0.2 02, the total secondary load is 2.4 and the power factor is 0.6. Determine if, on the occurrence of a fault, the error will exceed 10%.
Step by Step Solution
3.41 Rating (145 Votes )
There are 3 Steps involved in it
To determine if the error will exceed 10 on the occurrence of a fault we need to calculate the actua... View full answer
Get step-by-step solutions from verified subject matter experts