Question: The O . C and S . C test data are given below for a single phase, 2 0 kVA, 2 2 0 0 V

The O.C and S.C test data are given below for a single phase, 20kVA,2200V220V,50Hz transformer.
O.C test from LV side: 220V,4.2A,148W
S.C test from HV side: 74.5V,9.1A,270.4W;
20.Equivalent resistance referred to primary is
:
)3.27
B)0.0327
C)2.48
D)0.0248
21.Equivalent resistance referred to secondary is :
A)3.27
B)0.0327
C)2.48
D)0.0248
22. Equivalent reactance referred to primary is
(k)7.51
B)0.0751
C)9.36
:
23.Equivalent reactance referred to secondary is
D)0.0936
A)7.51
)0.0751
C)9.36
:
24. Regulation of transformer at 0.8 pf . lagging current is
A)3.57
B)3.93
C)2.94
25.Efficiency at full - load at 0.8 pf . lagging current is
A)97.71
B)97.77
(C)97.45
D)0.0936
26. Copper losses at half the full-load at 0.8 pf . lagging current is
A)320
B)80
C)270.4
W:
27. Core losses at half the full-load at 0.8 pf . lagging current is
A)148
B)296
C)74
w:
D)37
CS
For the network shown in the following figure, V1=15V;V2=30V
28. The output voltage V of the following circuit
A)5 V
B)25 V
C)12 V
)15 V
29. The current flow in the R1
A)0.05 A
B)0 A
C)0.15 A
D)0.2 A
30. The current flow in the R2
A)0.05 A
B)0 A
C)-0.15 A
D)-0.2 A
The O . C and S . C test data are given below for

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Electrical Engineering Questions!