Question: The S . C . test on a 1 - phase transformer, with the primary winding short - circuited and 3 0 V applied to

The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied to
the secondary gave a wattmeter reading of 60 W and secondary current of 10 A. If the normal applied
primary voltage is 200, the transformation ratio 1 :2 and the full-load secondary current 10 A, calculate
the secondary terminal p.d. at full-load current for (a) unity power factor (b) power factor 0.8 lagging.
If any approximations are made, they must be explained.