Question: Translated Statement: The selected cable can carry an effective current of 2 0 0 A . It powers a three - phase load network with

Translated Statement:
The selected cable can carry an effective current of 200 A. It powers a three-phase load network with a line-to-line effective voltage of 1 kV and a frequency of 60 Hz. There are three loads connected to the line.
Load 1 consists of three inductors of 8 mH connected in delta ().
Load 2 consists of three capacitors of 1.5 mF connected in star (Y).
Load 3 consumes an active power of 100 kW.
Finally, a synchronous machine operating in motor mode is connected at the end of the line. It delivers a power of 50 kW and is connected in star (Y). It has 8 poles and a synchronous reactance of 0.88.
a) If the synchronous machine operates at a unity power factor, determine if the selected cable's 200-ampere capacity is adequate. Support your choice with all required calculations.
b) If the synchronous machine has a constant KK of 9.5, the flux (\Phi) is 450 mWb, and the active power provided by this machine remains constant at 50 kW, determine whether the conductor's capacity is exceeded. Support your choice with all required calculations.
c) If the machine's flux (\Phi) produced by the excitation current (ifi_f) is given by the equation:
(if)=(0.05)(if)+0.25(Wb),\Phi(i_f)=(0.05)(i_f)+0.25\,\text{(Wb)},
determine the value of the excitation current allowing the selection of the smallest wire gauge. Assume that the synchronous machine still provides 50 kW of power and that the constant KK is 9.5. Support your choice with all required calculations.
i already done question a i juste need b and c

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Electrical Engineering Questions!