Question: ( 2 ) During a short circuit test, a Y - connected synchronous generator produces 1 0 0 A of short - circuit armature current

(2) During a short circuit test, a Y-connected synchronous generator produces 100 A of short-circuit armature current per phase at a field current of 2.5 A . At the same field current, the open-circuit line voltage is measured to be 440 V .
(a) Calculate the saturated synchronous reactance under these conditions.
(b) If the armature resistance is 0.3 per phase, and the generator supplies 60 A to a purely resistive Y-connected load of 3 per phase at this field current setting, determine the voltage regulation under these load conditions.
Open circutit
E1=490V
Sonat Cireui
=EAxS
t=440v1001=4.4
IA=ARA+jS
ismor; RA... I
vv+60A(0.3+j4.45)+Vp
440V-60A(4.91s)=v6175.3
( 2 ) During a short circuit test, a Y -