Question: 7 . 3 An equivalent source at 6 9 kV has a three - phase short - circuit capacity of 1 1 8 0 MVA

7.3 An equivalent source at 69 kV has a three-phase short-circuit capacity of 1180 MVA with X/R =10. It feeds a dedicated feeder through a 30 MVA, 69 kV/12.47 kV transformer with a leakage impedance of 5 percent. A data hotel whose loads primarily consist of computers and network servers is fed by a 1500 kVA, 12.47/480V service transformer. The leakage impedance is 4 percent. A capacitor bank is configured wye-grounded and installed at the secondary of the 69/12.47 kV transformer. The capacitor bank has an adjusted rating of 3.287 Mvar at 12.47 kV (line-line voltage). The nonlinear load has a fundamental current of 450 A and it produces 11th order harmonic current of 5.3 percent of the fundamental.