Question: A balanced three - phase load absorbs 2 3 0 . 4 4 kVA at a leading power factor of 0 . 8 when the
A balanced threephase load absorbs kVA at a leading power factor of when the line voltage at the terminals of the load is V Find four equivalent circuits that can be used to model this load Assume a connected load series Find the value of Z Now assume a Y connected load series Find the value of ZY Now assume a connected load parallel Find the values of R and X Now assume a Y connected load parallel Find the values of RY and XY