Question: A double - wound, 1 - phase transformer is required to step down from 1 9 0 0 V to 2 4 0 V ,

A double-wound, 1-phase transformer is required to step down from 1900 V to 240 V,50-Hz. It is
to have 1.5 V per turn. Calculate the required number of turns on the primary and secondary windings
respectively.
The peak value of flux density is required to be not more than 1.2 Wb/m2. Calculate the required
cross-sectional area of the steel core. If the output is 10 kVA, calculate the secondary current.
[1,267; 160; 56.4 cm2; 41.75