Question: A multi - use building is slated for design, with the following potential uses: What is the required live load for this building? From ASCE

A multi-use building is slated for
design, with the following potential uses:
What is the required live load for this
building?
From ASCE 7, Table 4.3-1:
The maximum uniformly distributed live load
for wholesale grocery (all floors) is 125 psf.
The maximum uniformly distributed live load
for dining rooms and
restaurants is 100 psf.
The maximum uniformly distributed live load
for library storage (falls under the Library -
Stack Rooms category) is 150 psf
Wholesale
Grocery A decorative statue is located at the third
story of the 8-story building shown below. Each
floor has a total height of 12'-6'' as indicated
below. What is the velocity pressure exposure
coefficient for this case, utilizing exposure
category B? A three story, steel moment
resisting frame building is located
on a site with a shear wave velocity
of 800ftsec. The 5% damped,
maximum considered earthquake
spectral response accelerations are
Ss=0.85g and S1=0.27g.
Determine the 5% damped design
spectral response accelerations SDS
and SD1.
SMS=faSS
SM1=FvS1
{fa=1.16
fx=2.06
SDS=23SMS
SD1=23SM1