Question: a Problem 4-Sinusoidal Response An engineer uses a temperature sensor mounted in a thermowell to measure the temperature in a CSTR. The temperature sensor/transmitter combination

a Problem 4-Sinusoidal Response An engineer uses a temperature sensor mounted in a thermowell to measure the temperature in a CSTR. The temperature sensor/transmitter combination operates approximately as a first-order system with a time constant equal to 3 s. The thermowell behaves like a first-order system with time constant of 10 s. The engineer notes that the measured reactor temperature has been cycling approximately sinusoidally between 180 and 183C with a period of 30 s for at least several minutes. What can be concluded concerning the actual temperature in the reactor
Step by Step Solution
There are 3 Steps involved in it
Get step-by-step solutions from verified subject matter experts