An energy auditor was only provided with the prior two years of electric utility data for a
Fantastic news! We've Found the answer you've been seeking!
Question:
An energy auditor was only provided with the prior two years of electric utility data for a facility. After studying the data, the energy auditor identified that the peak demand charges were the most significant portion of the utility bill. The monthly actual peak demand (in kW) and the rate structure for the facility are shown in Tables 1 and 2.
- Calculate the total and monthly billed demand charges for year 2020..
For this problem, the ratchet clause should be applied using 65% of the maximum actual demand corrected for power factor during the prior 11 months, and pfbase = 0.85 and pfactual = 0.75.